The 2.5mm² flex is too small for a 32A MCB.Double oven with a 4.9 kw load on 10mm cable (was supposed to be electric hob but changed to gas), 2.5mm cooker flex to switch with a 32amp MCB in CU Is this ok or does it need altering.
Of course you can.Can you get 4mm2 flex
Try here.not seen that anywhere
and doubt id get in terminals.
Simple answer it needs altering. However as we start to look more carefully then one has to question does it really? 2.5mm thermosetting cable clipped direct is rated 33A however unlikely it is clipped direct. The oven wants 21A and most MCB's ranges jump from 20A to 32A so either one slightly overloads a 20A or you use a 32A which would mean you need 4mm cable.Hi fellas
Double oven with a 4.9 kw load on 10mm cable (was supposed to be electric hob but changed to gas), 2.5mm cooker flex to switch with a 32amp MCB in CU Is this ok or does it need altering.
Cheers
If the manufacturer had read that, he might not even have necessarily asked for 4mm² cable (19A, or less, after diversity), although it probably would not be sensible to use anything less than 4mm² for a cooker circuit (and obviously essential with some installation methods).The manufacturer is correct. ... Nice maths.. but you forgot about diversity…. HAve a read about it here, and it will make mopre sense.
Not exactly, the circuit breaker will not trip at 32.1A.So diversity makes the assumption that one will not “max out” the circuit and if they do, the design will mean the circuit breakers will trip.
Diversity does not apply to ring final circuits.With regard to a ring main, with multiple 13 amp sockets, that assumption make perfect sense and of course reduces costs.
The 'Christmas' scenario is an oft used myth.With regard to the cooker, the manufacturer has also applied diversity, somewhat greater than the regs suggest, but in essence, the manufacturer is suggesting that one will not run the oven, grill and all four burners at the same time. I would argue this scenario should be catered for. Think Christmas lunch. Or is it a case that the cooker itself cannot handle this?
Are you sure it does not state a 32A supply minimum?I notice the manufacture states the fuse should be 32A minimum, so as I am adding a socket, I need to cater for this by increasing the fuse rating.
The 9.4kW will have been quoted at 240V so a slight reduction -In the link you provided (BS7671, OSG, Table 1B), when applying diversity for cookers in a domestic installation, diversity is calculate thus: 10A +30% f.l. + 5A (w/ socket).
The manufacturer specifies:
Burners: 1200W, 1700W, 1200W & 1700W (5800W)
Top oven: 1600W
Main oven: 2000W
Connected load: I = P/V = 9400W / 230V = 40.87A
Applying diversity = 10A + 30% x (40.87A – 10A) + 5A = 24.26A
Your maths has gone awry; that is 6,000W but even at 8,000W (33.3A) - It won't.So for arguments sake, let’s say I had the oven on, drawing 2000W, 1x 1700W burner and a 2300W kettle boiling away. The connected load would then be: 8000W/230V = 34A. My MCB has just tripped!
It depends what you mean by better.As I have the additional socket, would it not be better to go for a 40A MCB and 6mm2 cable?
In fact, fractionally less than even that if, per convention, one undertakes ones calculations at 230V ...The 9.4kW will have been quoted at 240V so a slight reduction - 9400W / 240V = 39.2A - 10 = 29.2A x 0.3 = 8.75 + 10 + 5 = 23.75A
Does if you have more than 1 - see R9C2 in Table 1B in the OSG.Diversity does not apply to ring final circuits.
It's about time you bought the green one.see R9C2 in Table 1B in the OSG.
Do we get a yellow one if we wait until next year (not far away!)?It's about time you bought the green one. It is a vast improvement.
....
I lied; it's just as bad.
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local