I know its been done to death but...
11.4 Kw freestanding oven and hob 49.5 a
Diversity brings it down to 21.85a (No socket)
Table A1 (OSG) First 10a of the rated current +30% of remainder
Table A2 10a + 30% f.l
These are slightly different one say rated current and one full load.
Could someone please explain.
And 6mm2 cable would fit all the criteria
5m run to CU clipped direct, no insulation. on a 32a MCB
I still feel odd about putting it on a 6mm2 cable, but putting it on 10mm would be unnecessary, wouldn't it? especially when fused at 32a
Thanks
11.4 Kw freestanding oven and hob 49.5 a
Diversity brings it down to 21.85a (No socket)
Table A1 (OSG) First 10a of the rated current +30% of remainder
Table A2 10a + 30% f.l
These are slightly different one say rated current and one full load.
Could someone please explain.
And 6mm2 cable would fit all the criteria
5m run to CU clipped direct, no insulation. on a 32a MCB
I still feel odd about putting it on a 6mm2 cable, but putting it on 10mm would be unnecessary, wouldn't it? especially when fused at 32a
Thanks