currently have electric oven and gas hob but looking to replace with new electric oven and hob.
Existing oven is 4.6kw fed by 6mm cable with 20amp mcb.
The cable is 2metres in plaster and approx 15metres loose laid in loft over insulation.
The new appliances will be rated 3.8kw and 7kw, so at max could take 45amps.
As I understand 6mm cable is rated 46amps, would it be ok to just upgrade mcb to 50amp?
I guess the alternative solution would be to use the existing supply for the 7kw hob and install a second 20a supply for the oven.