Cooker circuit is protected at consumer unit via a 40a fuse and has isolation switch within 2m and i have a outlet plate behind the cooker..Cooker will be fitted within 2m of isolation switch.
Cooker i am putting in is rated at 7.9kw
manual states min 25a fuse and cable to be 3x 2.5 mm2 or equivalent .
Trouble is i can get some heat resistant cable 2.5mm2 but it's rated at 25amps so would you use 4.mm2 which is rated at 35a ? The thing that bothers me is that the fuse is there for protecting the cable but none of the above are higher than my fuse in CU . I like to protect the cable from a possible over load if there were a fault with the appliance and the appliances internal protection did not work and the cable over heated ,so could i use 6mm2 as this is rated past my 40a fuse or would you consider replacing the cu fuse with a smaller one ?
I know about applying diversity but just wondering about the cable and cu fuse rating.
Cooker i am putting in is rated at 7.9kw
manual states min 25a fuse and cable to be 3x 2.5 mm2 or equivalent .
Trouble is i can get some heat resistant cable 2.5mm2 but it's rated at 25amps so would you use 4.mm2 which is rated at 35a ? The thing that bothers me is that the fuse is there for protecting the cable but none of the above are higher than my fuse in CU . I like to protect the cable from a possible over load if there were a fault with the appliance and the appliances internal protection did not work and the cable over heated ,so could i use 6mm2 as this is rated past my 40a fuse or would you consider replacing the cu fuse with a smaller one ?