correct cable sizing

Joined
20 Oct 2009
Messages
3
Reaction score
0
Country
United Kingdom
can you help i am about to fit a siemens continuius flow water heater which is 13.2 kw. The distance from the consumer unit to the water heater is aprox 30m. Can you advise me on the correct cable size that i require and what the correct RCD that i will require plz
 
Sponsored Links
I am competent but am unsure on the sizing of the cable can you assist plz
 
Sponsored Links
ahh cheers for that ive worked it out now myself i didnt realise i was on the wrong forum only been on here for first time today
 
13.2Kw = 57.3913A and volt drop max UK standard 11.5v so 11.5/57/30 = 6.7 mV/A/m nearest to that is 10mm sq at 4.4 mV/A/m but depending on run you may 16mm to carry current you did not say how run.
 
Sponsored Links
Back
Top