Good Evening All, I would like to pick your brain again please.
Scenerio being a test on a Ring final circuit. I completed the end to end readings they were fine, came to the cross link p1 to e2 p2 to e1.
There are eleven points on the circuit all of them came up fine apart from the last three, the readings where of 725 to 750 ohms.
I couldnt believe it so I opened up the face plates and took the readings with the probes on the screws still the same. Then I have unscrewed the cables out of the sockets thinking it could be some faulty sockets and took the readings again, they didnt change.
I do realise that there is a major fault on that side of the circuit, and will check for continuity between phase and earth without the crosslink.
Lucky for me there is nobody living there, so I could leave it isolated, however my question is if somebody was living there how would you go about it ?
I have heard you cant condemn the sockets, only advise the customer not to use them ?
If you were to blank them off with blank plates and crimp the cables or wago them, would that still not be dangerous as it is a Ring final circuit and them cables would still be in use ?
Last of all I might be missing something very simple here but why am I not getting high readings all the way around ?
Thank you in advance.
Scenerio being a test on a Ring final circuit. I completed the end to end readings they were fine, came to the cross link p1 to e2 p2 to e1.
There are eleven points on the circuit all of them came up fine apart from the last three, the readings where of 725 to 750 ohms.
I couldnt believe it so I opened up the face plates and took the readings with the probes on the screws still the same. Then I have unscrewed the cables out of the sockets thinking it could be some faulty sockets and took the readings again, they didnt change.
I do realise that there is a major fault on that side of the circuit, and will check for continuity between phase and earth without the crosslink.
Lucky for me there is nobody living there, so I could leave it isolated, however my question is if somebody was living there how would you go about it ?
I have heard you cant condemn the sockets, only advise the customer not to use them ?
If you were to blank them off with blank plates and crimp the cables or wago them, would that still not be dangerous as it is a Ring final circuit and them cables would still be in use ?
Last of all I might be missing something very simple here but why am I not getting high readings all the way around ?
Thank you in advance.