I have fitted a Danfoss HSA3 motorised valve to replace a honeywell with no head! Whoever removed the head from the honeywell has butchered the control wiring (I assume). The Danfoss "manual" is next to useless, I assume. Am I correct in thinking that the brown and blue wires in the danfoss are permanent live and neutral, Which of the other two (orange or grey) should be connected to the cylinder stat, and what does the other connect to. There is no room stat on the system. Am au fait with electricals and electronics but this heating lark is somewhat mystical. Cheers in advance
 
Sponsored Links
You've got it wrong. Look on the Danfoss or Honeywell web sites for details of wiring for S plan (2 x 2 port valves) and Y plan (1 x 3 port valve).

The control circuit is just a sequence of switches, but one of them is a microswitch in the valve connecting grey and orange. Generally Brown feeds from the stat controlling that valve. Blue is neutral. Grey may be permanent live and orange feeds back to boiler/pump, but don't just take my word or it - find and study the control circuit diagram.
 