Hi, current room stat is a SunVic - it has live and what appears to be 2 neutral connections.. when i replaced it with a new Danfoss the boiler fires but as soon as I adjust the Danfoss RMT-230 roomstat it blows heating fuse... any ideas please.. thanks in advance.. Andrew
 
Sponsored Links
Sounds as though you have wired it wrong.

I suspect the neutral has been connected to the switched live terminal by mistake.
 
As dave says wired wrong why would it have 2 neutrals,

Live IN
Live OUT
neutral/possibly earth

Picture of your existing might help
 
Sponsored Links
Blue is neutral, Yellow is switched live and Red is live. Drawing/ schematic does not show two neutrals- look again closely
 