K
kai
This is what I call a dangerous installation, the intake arrives at the front hall, in the form of a TNS 3 phase supply, That cut-out header only has solid copper links in it, the measured PFC comes to 46kA, which is about the average for every property in that North London street. The old supply feeder comes straight off an 400amp fused supply at the substation next door.
There are no switchfuses in the tails or indeed anywhere in the supply feed.
The rewireable consumer unit is situated inside the upstairs flat.
What do you think will happen if a 22kA fault developed? - The place will probably go up in flames, as the breaking capacity of a rewireable is only 1kA, far short of the supply 46kA PSCC.
It looks like a classic case for a full strip out and re-wire, in order to make it safe.