DC Fuse
11 Jun 2013
Yorkshire
I am working on a small project and need to fuse two outputs at 24v DC (2A) and 12v DC (2A). A panel building friend of mine has told me to use MCBs at 2A each but in my tests the breakers had no tripped at 2.9-3.1A and they were getting quite warm.
I would like your input on the best fuse for the job and why he thinks MCBs are OK to use?
Some manufacturers quote DC specs for their breakers - I recall reading about this on Merlin Gerin's site some time ago as I had an idea for a project (that didn't happen).
The thermal element should trip the same for DC as AC since AC currents are quoted as RMS. The magnetic trip may operate differently, but that possibly depends on the time constant of the magnetic circuit.
The breaking capacity is likely to be significantly lower on DC than on AC, and the voltage rating might be lower.
As SimonH2 has said, when using a standard AC MCB on DC, the magnetic trip behaviour will probably be different from that with AC, but the thermal trip should be essentially the same ...
However, I wonder how long you waited. A B2 MCB will take about 1 hour to trip (thermally) at 2.9A (I2 = 1.45*In) and, I imagine, not much less than an hour to trip at 3.1A.
Kind Regards, John
Its for a 24v control circuit that will power panel lights, timers and contactors etc
Where are you wanting to put these fuses/MCBs - between the power source and the 'panel'? If so, what sort of power source is it? If it's an 'electronic' mains-powered power supply, there could well already be adequate current limiting built into it (unless you're wanting 'belt and braces'). If it's 'car batteries', then you certainly would need a fuse!