Dedietrich DOD428XU11, oven blowing RCD trip. replaced element. Insulation resistance @500V 0.35Mohm. Any ideas , Thanks in anticipation.
 
Sponsored Links
I have read the other threads similar to this. It now seems that the grill comes on for a few minutes, then trips. We will try slowly warming up the grill to drive out any moisture. More degrees than a thermometer here. Thanks everyone
 
If its of interest/useful, my combined over/grill has top, rear and bottom grill elements. It was in the house I moved into 2 years ago and was tripping the RCD. On investigation, both the top and rear elements were both leaking to earth.

Its an old Kuppersbusch and the label was faded so I measured the elements, got the power ratings off the fixings and sourced new ones. The oven is now working well.

By the way 0.35MΩ is a very low reading for insulation resistance.
 
Sponsored Links
Thanks for you reply. We ran up the oven and now it is no longer tripping the RCD. Alls well that ends well.
 