There are 3 ways of doing EFLI measurement.
1) Calculation
- Ask DNO what service type & Ze (eg, TN-C-S & 0.35ohm)
- Measure R1+R2 (or r1+r2 etc as appropriate based on f.c. type)
- Zs = Ze + (R1+R2)
2) 20-25A whack via EFLI meter doing High Current EFLI test
- This requires a non-RCD protected circuit
- It does confirm at least the earth is better than carbon tracks
3) 15ma squeak via EFLI meter doing RCD no-Trip EFLI test
This is where the fun starts...
- Firstly your earth path might actually be carbon & vapourise before CPD disconnects the fault
- Secondly EFLI is calculated via a complex algorithm which is greatly affected by noise - sensitivity analysis is poor
Sensitivity...
Test is performed at 15ma, does not take much noise to affect your signal.
- Eg, any connected devices (washing machine, fridge, PC have filters) which can affect the result (and give a voltage on the line)
- Eg, any noise on the line from fluorescent circuits on the same CU/DB with CPD left "on" can affect the result (earlier Megger CM500/LT7 very sensitive here)
Accuracy...
Each machine has its own accuracy.
- Some are +/- 10%.
- Some are +/- 2.5% with 4 digits - so low impedance readings error margin is quite significant
Calibration...
Realise most meters are only calibrated at quite high impedance
- Calibration may be 0.72ohms displayed under 0.70ohm test
- Thus accuracy below that is subject to unknown error
Whats good on low current EFLI testing...
- Recent Fluke are actually quite reliable
- Megger MFT1552 etc are also well regarded
- Socket & See PDL200/234 & 310 are also consistent & accurate
- Older Megger CM500/LT7 can be too sensitive & unreproduceable
Good?
i) results from high-current tests are ball-park with low-current tests
ii) results are reproduceable. Sensitivity analysis is good
Batteries can be very important.
- Some machines suffer drift as batteries get down to half full
Low current tests are sensitive.
Sensitive to high noise, high harmonics, close to TX, lots of fluorescent lights, any loads left connected somewhere with filter networks (washing machines, alarms). As you get below about 0.7ohms they are indicative, and any really low reading (0.40ohm & below) on some meters can be fiction in that a high current test will give quite different results.
It can be annoying - on a TN-S supply it is easy to get into pass/fail/pass/pass/fail/fail on repeated tests with some low-current efli tests on high rated CPD. So if in doubt, bridge out & use a high current test (realising the risks). Alternatively measure Ze & then R1+R2 - the regs permit "dead calculation" which with a battery of RCBOs and a noisy supply might actually be necessary with some older meters.
So if you are finding low-current EFLI test results vary, I am not that surprised.
I recall a PDL-420 gave 0.40-0.62ohm on low current test for Zs, when an LT7 on high current test gave 0.21ohm (which was close to DNO test figure). The LT7 on low current test gave 0.6-0.8-1.2ohm, but its algorithm is known to be extremely sensitive. Some makers say check batteries are fresh & repeat test 3 times taking the average. I think even some of the older Fluke (1651?) benefited from that.
If that is a new DiLog I would perhaps look at the MFT 1552 etc.
I prefer 1-use machines (Megger for RCD, Robin for IR+Continuity).
The full set of tests is x0.5 (no trip), x1 (trip <200ms), x5 (trip <40ms), with test performed at 0-degree & 180-degree phase rotation (up/down cycles in AC voltage waveform). Some meters can not do the phase rotation bit, cutprice multi-testers leave some bits out (Kewtech?).