A builder recently asked me for a length of 10.0mm2 t+e cable so that he could put in the load for a 9.7kw shower so that he could carry on working in the bathroom as i couldn't get there for another week.
So now that the load for the shower is in and 'enclosed in capping inside a wall' which can have anything up to 52 amps running through it according to table 7.2 in the OSG, i've gone to the job to look at getting the supply in. The easiest way of doing this is by using the old 6mm2 as a draw wire but the only problem with this is that it is 'surrounded by thermal installation in a stud wall not touching a wall' at least i can't tell if it is touching a wall. So table 7.2 in the OSG says that a 10mm in this situation can only take 32 amps where as a 16mm can take 42.5 amps, which is what i'll need as i'll need a 40 amp mcb for the shower.
So finally would it be ok to have a 16mm2 supply for the shower switch and a 10mm2 load as putting in a 10mm2 as the supply would be a lot more time consuming and costly?
So now that the load for the shower is in and 'enclosed in capping inside a wall' which can have anything up to 52 amps running through it according to table 7.2 in the OSG, i've gone to the job to look at getting the supply in. The easiest way of doing this is by using the old 6mm2 as a draw wire but the only problem with this is that it is 'surrounded by thermal installation in a stud wall not touching a wall' at least i can't tell if it is touching a wall. So table 7.2 in the OSG says that a 10mm in this situation can only take 32 amps where as a 16mm can take 42.5 amps, which is what i'll need as i'll need a 40 amp mcb for the shower.
So finally would it be ok to have a 16mm2 supply for the shower switch and a 10mm2 load as putting in a 10mm2 as the supply would be a lot more time consuming and costly?