Chaps
I have been changing these mid position Myson MPE322 diverter valve actuator heads quite frequently and I know they are not the best design and suffer from overheating issues as they are just stalled and drawing current in the on position.
However on further investigation I have found that the valve is always in the CH position (except when hot water is called for then it drives to mid position). So for 24 hours a day 256 days a year this valve is in the CH position drawing current and remaining hot. Now wonder they aint lasting long!
The situation might not be helped because I have replaced the original with a Heat miser thermostat which is programmed to change the temperature setting for different times of the day. So on the controller the Central heating is set to continuous and the stat does the heating control. I just thought that when the stat goes off and there is no call for hot water, the diverter valve should loose all power and return under spring tension to it initial un-powered position but it doesn't, it remains powered in the CH position. Is this correct?
I have been changing these mid position Myson MPE322 diverter valve actuator heads quite frequently and I know they are not the best design and suffer from overheating issues as they are just stalled and drawing current in the on position.
However on further investigation I have found that the valve is always in the CH position (except when hot water is called for then it drives to mid position). So for 24 hours a day 256 days a year this valve is in the CH position drawing current and remaining hot. Now wonder they aint lasting long!
The situation might not be helped because I have replaced the original with a Heat miser thermostat which is programmed to change the temperature setting for different times of the day. So on the controller the Central heating is set to continuous and the stat does the heating control. I just thought that when the stat goes off and there is no call for hot water, the diverter valve should loose all power and return under spring tension to it initial un-powered position but it doesn't, it remains powered in the CH position. Is this correct?