After finding and fixing a burnt through cable due to incompetent fitting of wiring in my Mother's kitchen (previous post), I decided it should be checked out and though I'd use the chance to try out my shiny new Megger MFT1552.
However, as I half expected, the testing suggests there are problems so I would appreciate running the results past you and seeking advice on my current conclusions.
The situation is that two older 2.5mm2 cables leave the CU - at some point under the floor I assumed they were joined to the kitchen 'ring' which is wired in grey (old colour cores) 2.5mm2.
I started at the CU and got the following:
Phase Continuity r1 : 0.22
CPC Continuity r1 : 0.31
so far so simple
Then the Neutral Continuity rn gave me no continuity (>999MOhm)
Given that the sockets all work correctly and all seem to be wired to correct polarity, I formed the conclusion that either one of the cable joins had a faulty neutral link, hence making the circuit effectively a long radial (running on a 30A MCB), or there was a Neutral break somewhere between sockets making it 2 radials (alebit with a complete Phase conductor)
I proceeded anyway and tested at the sockets, initially P-E (R1 + R2) with opposite Phase and Earth linked which gave readings of between 0.18 and 0.23 at the sockets, and up to 0.38 on what I think are spurred sockets - suggesting that there was a ring of sorts.
The Phase-Neutral readings with Phase-Neutrals linked ranged from 0.23 to 0.36 at the sockets.
I then tried to check my theory, so disconnected and electricall separated each individual core at the CU for this particular ring (I double checked and confirmed they were the correct cores).
I then opened a socket and did the following continuity tests:
Neutral to Neutral : 0.14 Ohm
Phase to Phase : 0.14 Ohm
and I then tested
Neutral to Phase and Phase to Neutral of the two incoming 'ring' cables, which both gave a reading of 8.43 Ohm....
At this point my headache started so I put everything back as it was and sat down with paper to draw it out.
Using my vast inexperience and some logic, my most likely situation is that the two ring ends from the CU and the two ring ends from the kitchen are joined together in one junction box, hence forming a small electrical ring in the kitchen, but connected together with with the two incoming legs from the CU, one of which may well not make proper connection between Neutrals, hence the lack of continuity on Neutral but not Phase at the CU.
Unless I'm missing something this is a 'bad thing' and I need to locate and change this end up with just the two legs feeding the ring and returning separately to the CU..
Sorry for rambling a little, but I hope I have given enough information to make sense.
If I'm missing an alternative possibility, I'd appreciate suggestions and the best way of testing to confirm before I have to dig up my Mother's nice kitchen floor!
I can draw a diagram if that would help, but not sure how much it would add to the above.
I should just add that the competence of the installer is perhaps shown by the running of 4mm2 cable from a 40A MCB to the double Gas oven, which the manual states requires a 3A FCU. I can only give him the benefit of the doubt that he ran it in case a later user wants an electric oven..
Many Thanks for any assistance - I am sure that the vast experience of the forum will find this an easy challenge (yes that was me creeping ).
Gavin
However, as I half expected, the testing suggests there are problems so I would appreciate running the results past you and seeking advice on my current conclusions.
The situation is that two older 2.5mm2 cables leave the CU - at some point under the floor I assumed they were joined to the kitchen 'ring' which is wired in grey (old colour cores) 2.5mm2.
I started at the CU and got the following:
Phase Continuity r1 : 0.22
CPC Continuity r1 : 0.31
so far so simple
Then the Neutral Continuity rn gave me no continuity (>999MOhm)
Given that the sockets all work correctly and all seem to be wired to correct polarity, I formed the conclusion that either one of the cable joins had a faulty neutral link, hence making the circuit effectively a long radial (running on a 30A MCB), or there was a Neutral break somewhere between sockets making it 2 radials (alebit with a complete Phase conductor)
I proceeded anyway and tested at the sockets, initially P-E (R1 + R2) with opposite Phase and Earth linked which gave readings of between 0.18 and 0.23 at the sockets, and up to 0.38 on what I think are spurred sockets - suggesting that there was a ring of sorts.
The Phase-Neutral readings with Phase-Neutrals linked ranged from 0.23 to 0.36 at the sockets.
I then tried to check my theory, so disconnected and electricall separated each individual core at the CU for this particular ring (I double checked and confirmed they were the correct cores).
I then opened a socket and did the following continuity tests:
Neutral to Neutral : 0.14 Ohm
Phase to Phase : 0.14 Ohm
and I then tested
Neutral to Phase and Phase to Neutral of the two incoming 'ring' cables, which both gave a reading of 8.43 Ohm....
At this point my headache started so I put everything back as it was and sat down with paper to draw it out.
Using my vast inexperience and some logic, my most likely situation is that the two ring ends from the CU and the two ring ends from the kitchen are joined together in one junction box, hence forming a small electrical ring in the kitchen, but connected together with with the two incoming legs from the CU, one of which may well not make proper connection between Neutrals, hence the lack of continuity on Neutral but not Phase at the CU.
Unless I'm missing something this is a 'bad thing' and I need to locate and change this end up with just the two legs feeding the ring and returning separately to the CU..
Sorry for rambling a little, but I hope I have given enough information to make sense.
If I'm missing an alternative possibility, I'd appreciate suggestions and the best way of testing to confirm before I have to dig up my Mother's nice kitchen floor!
I can draw a diagram if that would help, but not sure how much it would add to the above.
I should just add that the competence of the installer is perhaps shown by the running of 4mm2 cable from a 40A MCB to the double Gas oven, which the manual states requires a 3A FCU. I can only give him the benefit of the doubt that he ran it in case a later user wants an electric oven..
Many Thanks for any assistance - I am sure that the vast experience of the forum will find this an easy challenge (yes that was me creeping ).
Gavin