Could anyone confirm that I'm right to be alarmed about the state of my shower installation (fitted b4 I bought the house):
It's 9.5kW; 6mm cable run about 8 metres
No isolator switch,
No RCD,
and originally on a 30a rewireable fuse (!!!)
Now, I converted the old Wylex rewire fuses to MCBs as soon as I moved in, so it's now on a 32a mcb.
Can anyone tell me if I'm on the right lines thinking that:
#An RCD is a VERY good idea (the CU doesn't have one);
#An isolation switch (double pole?) is a Very good idea (or does the removabe MCB cover this (though not the double pole issue));
#6mm cable is borderline at best (though the regs do allow up to 46a for ref method 1, which is this one);
#The MCB sums don't add up - (9500/230 = 41.3a or 9500/240 = 39.6a) so why is the 32a mcb not tripping? Am I getting away with it because I rarely have the shower on full heat?
Your opinions are appreciated
It's 9.5kW; 6mm cable run about 8 metres
No isolator switch,
No RCD,
and originally on a 30a rewireable fuse (!!!)
Now, I converted the old Wylex rewire fuses to MCBs as soon as I moved in, so it's now on a 32a mcb.
Can anyone tell me if I'm on the right lines thinking that:
#An RCD is a VERY good idea (the CU doesn't have one);
#An isolation switch (double pole?) is a Very good idea (or does the removabe MCB cover this (though not the double pole issue));
#6mm cable is borderline at best (though the regs do allow up to 46a for ref method 1, which is this one);
#The MCB sums don't add up - (9500/230 = 41.3a or 9500/240 = 39.6a) so why is the 32a mcb not tripping? Am I getting away with it because I rarely have the shower on full heat?
Your opinions are appreciated