Hi everyone,
Been using this forum at various times in the past and found it very helpful. Only just registered today as I need some advice, so this is my first post. Hope I am posting in the correct section.
We had the asbestos ceiling in our garage professionally removed a short while back and I am about to renew it. There are 2 bedrooms over the garage, so I know that it needs to be replaced with fire protection board.
I called British Gypsum Tech Support today and they were quite helpful.
I was hoping that they did a board that had both fire protection and insulation properties, but unfortunately they do not.
I was told that both 12mm and 15mm Fireline was 30 minute rated, which I suspected, so am looking at fixing a double layer. This will give me 1 hour rating.
The garage is 8M x 2.45M and I know that I have to offset all the joints. The spacing between the joists in 370mm and they run width ways. I was told that the fixing centres should be 230mm centres.
1) Can I get away with using 370mm centres going lengthways? I hope so as the original timbers are on joist hangers.
2) Can I screw through both boards rather than fixing the first board seperately? If so, what size screws would I need?
I'm also looking at hiring a panel lifter for the day to make the job that much easier.
Any advice will be greatly appreciated.
Been using this forum at various times in the past and found it very helpful. Only just registered today as I need some advice, so this is my first post. Hope I am posting in the correct section.
We had the asbestos ceiling in our garage professionally removed a short while back and I am about to renew it. There are 2 bedrooms over the garage, so I know that it needs to be replaced with fire protection board.
I called British Gypsum Tech Support today and they were quite helpful.
I was hoping that they did a board that had both fire protection and insulation properties, but unfortunately they do not.
I was told that both 12mm and 15mm Fireline was 30 minute rated, which I suspected, so am looking at fixing a double layer. This will give me 1 hour rating.
The garage is 8M x 2.45M and I know that I have to offset all the joints. The spacing between the joists in 370mm and they run width ways. I was told that the fixing centres should be 230mm centres.
1) Can I get away with using 370mm centres going lengthways? I hope so as the original timbers are on joist hangers.
2) Can I screw through both boards rather than fixing the first board seperately? If so, what size screws would I need?
I'm also looking at hiring a panel lifter for the day to make the job that much easier.
Any advice will be greatly appreciated.