Hi all,
I have a double oven which would be rated at approx 5.5kw (based upon the KW of spare elements as I have no manual) connected via a cooker connection unit fed from a 45A DP switch. The wiring is in 6mm2 embedded within the plaster for 500mm and then in capping for 1m and is about 1.5 metres from the consumer unit.
I also now have a 6.6KW hob to replace a gas hob which I need to connect to the supply. Can I connect the hob to the same wall plate as the oven and use a diversity calculation and do I need another separate cooker connection unit for the hob?
Should I uprate the cable to 10mm2 and leave as radial or could I 'ring' the circuit in 6mm2 back to the CU and have a 45A MCB.
I wouldn't think that this an uncommon scenario and advice would be appreciated. Thanks
I have a double oven which would be rated at approx 5.5kw (based upon the KW of spare elements as I have no manual) connected via a cooker connection unit fed from a 45A DP switch. The wiring is in 6mm2 embedded within the plaster for 500mm and then in capping for 1m and is about 1.5 metres from the consumer unit.