Hi folks,

I'm installing a Neff double oven rated 5.1kW @240V.

Would a 6mm t&e radial via an oven switch back to the cu on a 32a MCB be OK?

The cable will be around 5m long and will be burried into the wall for 2m and between ceiling and upstairs floor for 3m.

Thanks.
 
Sponsored Links
Yep 6mm is fine, 32A breaker is fine. 6mm can carry 46A when clipped direct and 32A if enclosed in an insulated wall so your ok for both. 5m run is fine in terms of Volt Drop. FYI your drawing a little over 22A
 