Downlighters in thermal insulation

Joined
31 Mar 2006
Messages
20,028
Reaction score
1,393
Location
Leeds
Country
United Kingdom
Got called to a job today where the MCB for the upstairs lights was tripping as soon as the bathroom lights were switched on.

I found three ELV downlighters completely surrounded in thermal insulation.

I found the fault was a cable which had been toasted due to being ontop of the DL lamp, and there being no where for the heat to go.

dl3.jpg


dl4.jpg


There is a clue to how hot these lights have been getting as the actual fittings have melted, and the plasterboard disintegrated around them :eek: :eek:

dl1.jpg


dl2.jpg



(Sorry about the picture quality. I only had my camera phone with me)
 
Sponsored Links
seen a few cast ones distorted recently, never realised how hot they actually get, surprised theres not more fires.

can see things getting worse with all this insulation being pushed.
 
But you just try and tell people not to install them... :evil:

I really cannot understand why halogen MR16 lamps, both LV and ELV were not the first ones to be banned.
 
I've seen a good few similar situations recently, albeit not as severe. I put down these installs as at risk, advise the customers not to use them and leave a letter. As I leave, I see the lights being turned back on.

:rolleyes:


My favourite is the downlighter cut into the joist.

Or downlighters with plastic pipe and/or cable immediately above them: at least there's a ready-made sprinkler system to put it out when it does go up...
 
Sponsored Links
I made the mistake of having ELV's fitted in the lounge, kitchen, hallways and shower room plus bathrooms in our bungalow, 49 in total.

We have had one very small fire above the kitchen ceiling where the sparks had used a chock block instead a jb. It was found under the 270mm of insulation. The block and cable to the transformer had been alight scorching the plasterboard as in your photo's.

Heatloss from the "ventilated" ceilings into the roof space is massive because of the need to keep the insulation away from these fittings we want to replace them but what with? LED's plus drivers £££
 
Why not use these, this is showing only one half of the cover for illustration purposes;
JC94020A.JPG
 
do any of these covers successfully keep the transformer away from both the downlighter and the insulation?

of course nowadays they tend to use insulation between floors ie between the downstairs ceiling and the upstairs floor of new houses. also between the suspended plasterboard ceiling and concrete slabs of new blocks of flats.
 
What sort of person would allow the situation to get as bad as in those photos?! Aesthetically, it looks absolutely p*ss-poor, you'd think that would have been enough to make most people sort out the problem well before things got to the stage where the circuit ceased to work.
 