- Joined
- 18 Feb 2007
- Messages
- 1,367
- Reaction score
- 77
- Country
I have a problem identifying a power drain on my domestic electric supply.
This is bugging me ‘cos I can’t find the source of this small electrical drain of 100 watts.
I have recently acquired a supply monitor which works simply by having a current transformer on the supply live and an electronic device which monitors real time energy usage. I wanted to check very crudely that a new digital electric meter was at least getting the same order of consumption that I measured. Which I might add does with in reasonable limits.
Now for the problem. I detected a drain on my supply of 100 watts with everything I could think of isolated. I searched for the source of this 100 watts so as to identify what was causing it. What I determined was that by Isolating the downstairs sockets at the consumer unit, the drain went immediately to zero, so at least I could determine that all upstairs circuits and all lighting circuit and garage were not the cause of this 100 watt drain.
Easy I hear you say, the cause must be some items on standby such as Computers, Printer, TV’s, DVD recorders, Micro Wave oven, Cooker, maybe fridges or freezers switching on. So I was determined to identify the source of the drain just for my own curiosity, so I systematically went to each and every socket and spur outlets through the downstairs of the house. This entailed switching off ALL of the devices to which I referred earlier. Still I had a 100 watt drain. I then thought I must have been mistaken when I isolated the downstairs sockets at the consumer unit. So I once again Isolated this circuit and immediately the drain went to zero. Re-established the ring main and the drain re-appeared.
Now I am at a loss to determine what is the source of this drain is, as I systematically switched each and every outlet off and still could not eliminate the 100 watt drain.
So there must be another circuit attached to the downstairs socket ring main which is the source of this power drain. Items such as Intruder alarm is supplied from the Upstairs circuits so it is not that.
There is no Earth leakage as I have RCD (Residual Current Detection) devices on the Ring Mains which trip with 20mA earth leakage, so there is no earth leakage.
I have ran out of ideas now.
With the wealth of knowledge and experience out there, has anyone any suggestions as to what this drainage could be. There must be something else supplied from this ring main of which I am unaware.
OK 100 watts is not that much but it amounts to about 2.5kwh per day or 10 kwh per week or 500 kwh per year which amount to about £70 per year. Not a bank breaker but worth identifying I feel.
Has anyone any suggestions?
This is bugging me ‘cos I can’t find the source of this small electrical drain of 100 watts.
I have recently acquired a supply monitor which works simply by having a current transformer on the supply live and an electronic device which monitors real time energy usage. I wanted to check very crudely that a new digital electric meter was at least getting the same order of consumption that I measured. Which I might add does with in reasonable limits.
Now for the problem. I detected a drain on my supply of 100 watts with everything I could think of isolated. I searched for the source of this 100 watts so as to identify what was causing it. What I determined was that by Isolating the downstairs sockets at the consumer unit, the drain went immediately to zero, so at least I could determine that all upstairs circuits and all lighting circuit and garage were not the cause of this 100 watt drain.
Easy I hear you say, the cause must be some items on standby such as Computers, Printer, TV’s, DVD recorders, Micro Wave oven, Cooker, maybe fridges or freezers switching on. So I was determined to identify the source of the drain just for my own curiosity, so I systematically went to each and every socket and spur outlets through the downstairs of the house. This entailed switching off ALL of the devices to which I referred earlier. Still I had a 100 watt drain. I then thought I must have been mistaken when I isolated the downstairs sockets at the consumer unit. So I once again Isolated this circuit and immediately the drain went to zero. Re-established the ring main and the drain re-appeared.
Now I am at a loss to determine what is the source of this drain is, as I systematically switched each and every outlet off and still could not eliminate the 100 watt drain.
So there must be another circuit attached to the downstairs socket ring main which is the source of this power drain. Items such as Intruder alarm is supplied from the Upstairs circuits so it is not that.
There is no Earth leakage as I have RCD (Residual Current Detection) devices on the Ring Mains which trip with 20mA earth leakage, so there is no earth leakage.
I have ran out of ideas now.
With the wealth of knowledge and experience out there, has anyone any suggestions as to what this drainage could be. There must be something else supplied from this ring main of which I am unaware.
OK 100 watts is not that much but it amounts to about 2.5kwh per day or 10 kwh per week or 500 kwh per year which amount to about £70 per year. Not a bank breaker but worth identifying I feel.
Has anyone any suggestions?