Our heating has two 2 port valves for heating and hot water, each with a switch that closes when the valve is near to fully open. These switches are in parallel with one side permanent live and the other side signalling to the pump and boiler.
Early last year the switch in the CH actuator started playing up, staying closed when the heating switched off so that the pump and boiler continued to run even though the valve was closed. At the time I replaced the actuator with new, and also replaced the microswitch in the faulty actuator to keep it as spare.
https://www.diynot.com/diy/threads/...e-actuator-faulty-switch.538791/#post-4551863
Now it's playing up again. The fault is intermittent and whenever I test things both actuators work perfectly, so I have only ever "seen" the fault when it's all wired up and live, so I have no way of knowing which of the two is at fault. Since I'd replaced the CH actuator I made a guess and swapped the HW one for the repaired unit, but that hasn't improved things.
Furthermore the fault itself shows itself strangely, with the switch correctly going off when the valve closes, but coming back on again of its own accord sometime later. Not what I'd expect if the switch was sticking. Three times now the system has shut down normally with pump and boiler stopping, only for the system to come on of its own accord once at 03:00 AM and once at 04:45, the third time I switched off the power in the evening after it had shut off on the timer. Then when I switched power back on in the morning the pump/boiler immediately started.
Any ideas on tracking down the issue? I don't really like leaving the system so might run for a long time in that faulty state as it can't be good for either pump or boiler running with both valves closed. However I can't see any alternative to waiting until it goes into that failed state, then investigating and testing live to see which switch is at fault. I say live because based on experience if I remove power the fault immediately clears.
Any comment welcome, Tony S
Early last year the switch in the CH actuator started playing up, staying closed when the heating switched off so that the pump and boiler continued to run even though the valve was closed. At the time I replaced the actuator with new, and also replaced the microswitch in the faulty actuator to keep it as spare.
https://www.diynot.com/diy/threads/...e-actuator-faulty-switch.538791/#post-4551863
Now it's playing up again. The fault is intermittent and whenever I test things both actuators work perfectly, so I have only ever "seen" the fault when it's all wired up and live, so I have no way of knowing which of the two is at fault. Since I'd replaced the CH actuator I made a guess and swapped the HW one for the repaired unit, but that hasn't improved things.
Furthermore the fault itself shows itself strangely, with the switch correctly going off when the valve closes, but coming back on again of its own accord sometime later. Not what I'd expect if the switch was sticking. Three times now the system has shut down normally with pump and boiler stopping, only for the system to come on of its own accord once at 03:00 AM and once at 04:45, the third time I switched off the power in the evening after it had shut off on the timer. Then when I switched power back on in the morning the pump/boiler immediately started.
Any ideas on tracking down the issue? I don't really like leaving the system so might run for a long time in that faulty state as it can't be good for either pump or boiler running with both valves closed. However I can't see any alternative to waiting until it goes into that failed state, then investigating and testing live to see which switch is at fault. I say live because based on experience if I remove power the fault immediately clears.