Hi all!
Had no heating the other morning. Boiler runs fine and I found that the HW was hot.
Seems that the ma-1 valve is not moving to the CH position. Putting it manually into CH got the house warm (so boiler/thermostat/wiring OK). The spindle in the pipe moves freely so not a locked up valve. The valve head manual override moves freely with the usual whirring sound.
I took off the head and made all for CH and no movement from the valve head. So I took the head apart.
Springs are still working and anchored correctly. That's good!
The motor reads 2500ohms approx, so not open circuit.
Anyone with any experience of these have any insight?
Thanks
Had no heating the other morning. Boiler runs fine and I found that the HW was hot.
Seems that the ma-1 valve is not moving to the CH position. Putting it manually into CH got the house warm (so boiler/thermostat/wiring OK). The spindle in the pipe moves freely so not a locked up valve. The valve head manual override moves freely with the usual whirring sound.
I took off the head and made all for CH and no movement from the valve head. So I took the head apart.
Springs are still working and anchored correctly. That's good!
The motor reads 2500ohms approx, so not open circuit.
Anyone with any experience of these have any insight?
Thanks