Just wanted to tell you guys about a fault that occurred on my CH /HW System using the Drayton 3 port mid position valve.
The problem was that my CH system would come on, but would continue to run at full tilt ignoring the room stat, or switching the CH off from the programmer. The only way I could stop the whole house getting very hot was to kill the mains to the whole system. H/W worked fine, with the tank stat controlling the temperature.
After some head scratching I disconnected the room stat output, and measured the CH Call voltage. When the fault occurred there was around 95V AC on the boiler input/call terminal.
The question was where was this coming from? I replaced the boiler control PCB just to ensure there was not a problem on the PCB outputting AC on the terminal, this made no difference. I checked the wiring in the junction box and everything looked ok. Looking at the circuit for the mid position valve I concluded that maybe one of the switches in the actuator was faulty, and the voltage was coming from there. Further inspection inside the actuator I spotted the black plastic arm that clips onto the valve/motor actuator arm had split, so although the valve moved, the switch was not being actuated by the cam on the end of the arm, hence stayed closed and put 230v through the call circuit continually. Replacement of the whole actuator has solved the problem. Had me scratching my head for some time though...
The problem was that my CH system would come on, but would continue to run at full tilt ignoring the room stat, or switching the CH off from the programmer. The only way I could stop the whole house getting very hot was to kill the mains to the whole system. H/W worked fine, with the tank stat controlling the temperature.
After some head scratching I disconnected the room stat output, and measured the CH Call voltage. When the fault occurred there was around 95V AC on the boiler input/call terminal.
The question was where was this coming from? I replaced the boiler control PCB just to ensure there was not a problem on the PCB outputting AC on the terminal, this made no difference. I checked the wiring in the junction box and everything looked ok. Looking at the circuit for the mid position valve I concluded that maybe one of the switches in the actuator was faulty, and the voltage was coming from there. Further inspection inside the actuator I spotted the black plastic arm that clips onto the valve/motor actuator arm had split, so although the valve moved, the switch was not being actuated by the cam on the end of the arm, hence stayed closed and put 230v through the call circuit continually. Replacement of the whole actuator has solved the problem. Had me scratching my head for some time though...