This 28 mm 2-port valve is just over a year old and therefore has a detachable actuator. It is one of two Drayton 2-port motorised valves for this Drayton "Lifestyle Plan" of central heating layout. The dhw valve is a similar Drayton one, but a 22 mm.
For some time we have found radiators getting warm when the central heating side of the system is off, but when the dhw side is on and the cylinder thermostat is calling for heat (so the pump is running). This was not a problem with the original ZA6 (before this failed, owing to the valve spindle having gone very stiff). Nor was it, at first, with the present ZA6. It is nothing to do with the system design, which is the standard layout for this type and is well executed.
I have experimented by removing the actuator and holding the valve spindle very firmly in the closed position by clamping a very small adjustable spanner to it and putting pressure on this to hold the swinging valve paddle firmly in the closed position - using a piece of cord.
This showed that the valve is capable of closing completely. When the pump was running for the dhw, the pipe below the ZA6 was cold.
If I refit the actuator, which works correctly and appears to exert a pretty strong return spring pressure on the valve spindle (to hold it shut when the valve is off), when the dhw valve opens and the pump starts (lowest of the three speeds), the pipe below the ZA6 rapidly gets very hot. Clearly the valve is letting water past.
Possibly the problem is one of valve design. I have shown that the swinging paddle in the valve body is capable of holding its neoprene pad firmly enough against the port to keep the valve completely closed. But, in practice, it seems that the return spring pressure exerted by the actuator is not powerful enough to resist the pump pressure. The pump is normally on its slowest speed and the dhw circuit is all 22 mm pipe and has no modulating valve in it.
It is tiresome and expensive to have to change this valve yet again. Should I first try a new actuator, in case the present one is actually faulty rather then simply not exerting enough spring pressure? Even this is not a cheap solution, though it is far less trouble than changing the whole valve!
Or should I fit a Sunvic 28 mm valve in place of the Drayton? We have a Sunvic 2-port valve on a zone. This valve uses spring pressure to close it, but does not have a swinging paddle. It has a rotating cylinder (operating along the same lines as the ball in a ball-type gate valve or "Ballofix" valve). Therefore, when it is closed, it cannot be forced partly open by pump pressure.
For some time we have found radiators getting warm when the central heating side of the system is off, but when the dhw side is on and the cylinder thermostat is calling for heat (so the pump is running). This was not a problem with the original ZA6 (before this failed, owing to the valve spindle having gone very stiff). Nor was it, at first, with the present ZA6. It is nothing to do with the system design, which is the standard layout for this type and is well executed.
I have experimented by removing the actuator and holding the valve spindle very firmly in the closed position by clamping a very small adjustable spanner to it and putting pressure on this to hold the swinging valve paddle firmly in the closed position - using a piece of cord.
This showed that the valve is capable of closing completely. When the pump was running for the dhw, the pipe below the ZA6 was cold.
If I refit the actuator, which works correctly and appears to exert a pretty strong return spring pressure on the valve spindle (to hold it shut when the valve is off), when the dhw valve opens and the pump starts (lowest of the three speeds), the pipe below the ZA6 rapidly gets very hot. Clearly the valve is letting water past.
Possibly the problem is one of valve design. I have shown that the swinging paddle in the valve body is capable of holding its neoprene pad firmly enough against the port to keep the valve completely closed. But, in practice, it seems that the return spring pressure exerted by the actuator is not powerful enough to resist the pump pressure. The pump is normally on its slowest speed and the dhw circuit is all 22 mm pipe and has no modulating valve in it.
It is tiresome and expensive to have to change this valve yet again. Should I first try a new actuator, in case the present one is actually faulty rather then simply not exerting enough spring pressure? Even this is not a cheap solution, though it is far less trouble than changing the whole valve!
Or should I fit a Sunvic 28 mm valve in place of the Drayton? We have a Sunvic 2-port valve on a zone. This valve uses spring pressure to close it, but does not have a swinging paddle. It has a rotating cylinder (operating along the same lines as the ball in a ball-type gate valve or "Ballofix" valve). Therefore, when it is closed, it cannot be forced partly open by pump pressure.