Earth fault with a boiler

Joined
19 Feb 2018
Messages
6
Reaction score
1
Country
United Kingdom
Hi

I am fairly sure we have an earth fault with our boiler. Every time we put our boiler on it either stays on for about 5 mins then trips out our electrics (the whole house). We have been told by an electrician thats its an earth fault. But a plumber has said that its unlikely to be the boiler as it has 2 fuses to stop the circuit board blowing up ? We have now had 2 electricians out and a plumber and we seem to be in no mans land ! We have had the boiler off for 4 days now and the electrics havent tripped out once. Any ideas or suggestions please. Thanks - Paul
 
Sponsored Links
What is printed on the thing that trips? All the letters and numbers. Post a photo of it please.

Is your boiler powered though a plug and socket, or a fused wall switch?

Earth leakage faults are most often associated with water getting into electrical parts.

Boilers sometimes have internal water leaks, but carefully inspect your circulating pump and your 3-port valve if they are outside the boiler, for example in an airing cupboard.

Boiler fuses protect against overcurrent. They are almost entirely irrelevant to earth leakage faults. Your heating engineer sounds surprisingly ignorant.
 
Hi John

Its tripping out at the Distribution Board - (the main fuse box in our garage). Would you recommend getting another heating engineer as opposed to an electrician ? Thanks - Paul
 
Sponsored Links
Its tripping out at the Distribution Board - (the main fuse box in our garage).

I still want to see the device that trips, and to know what's printed on it. I could guess, but that's not a good approach.
 
http://s119.photobucket.com/user/ooh_bugster/media/0JcJGBXFTXuVEs1MLTwMHw.jpg.html?sort=3&o=0

this is the RCD that is 'tripping out

'http://s119.photobucket.com/user/ooh_bugster/media/0JcJGBXFTXuVEs1MLTwMHw.jpg.html?sort=3&o=0

0JcJGBXFTXuVEs1MLTwMHw.jpg.html
 
OK, it is a 30mA RCD, as expected.

It looks like it might protect the whole house, which is now considered poor design, as there may be multiple small leakages on several circuits which together approach the trip level. Stand back and photograph the whole CU please.

Is your boiler powered via a plug and socket, or by a fused switch on the wall?
 
Make and model of boiler NEEDED
Sorry about the capitals
It is like getting into a taxi and telling the driver to take you home.
 
Maybe a water leak somewhere inside the boiler.
Did the plumber chap take the casing off and have a look inside?
Not all plumbers are good with finding faults inside boilers. Find a boiler break down engineer instead.
 
a plumber and 2 electricians and still no result , FFS's .
why dont you try a service and repair engineer ;)
 