ColJack said:could be any number of reasons..
cable size too small, cable run too long, lose or burnt connections on live or earth, broken leg on a ring etc...
could also be a socket fed of a fused spur from a ring with the fuse raising the live resistance...
disconnect from board and check circuit continuity and compare values..
earth value should be 3/5ths ( ration of 1.5 to 2.5 ) the value of the live and neutral.
Chivers7 said:could also be a faulty socket.
Other way up I think - 2.5 to 1.5 since the earth conductor is smaller - so its resistance will be higher - 1.67xLive for 2.5T&E
I get there and discover the Zs is fine from the socket terminals. All the sockets in that room (60's Volex) were sloppy, causing very poor readings.
ColJack said:I get there and discover the Zs is fine from the socket terminals. All the sockets in that room (60's Volex) were sloppy, causing very poor readings.
isn't that the point though..
if it's a high reading at the socket front, and the fault is on the appliance then the Zs will still be high back to the breaker causing longer disconnect times?
although theoretically it should take the fuse in the plug first..
if it's good on the terminals but bad on the socket front I would recommend changing the socket outlets to new ones..
Taylortwocities said:Mates he's got high Zs. If its that high the fuse isn't going to blow in the event of an earth fault.
ColJack said:yes it should..
discrimination..