struggling with a earth loop reading.
have a split load consumer unit. 100A breaker with 3 light circuits and boiler on one side and a 63a 30ma rccb with 3 ring mains and cooker circuits on the other side. originally i got called out for a tripping mcb and rcd on the kitchen ring when they overloaded the ring. did a quick check on the Zs and got 4.56 from every socket in the kitchen - then did a check on the other rings on the RCD, all about the same figure. did a Ze test (all good 0.18). stripped down the neutral busbar and earths from the mcbs and did a Zs test on the busbar (4.56 again) changed RCD but still same problem. meggered the rcd circuits - all good apart from kitchen ring L-PE 85.4Ohms on 500v - but still shouldnt cause such high results on the other Zs? any suggestions?? apparantly no pictures hooks or nails have been banged in either.
have a split load consumer unit. 100A breaker with 3 light circuits and boiler on one side and a 63a 30ma rccb with 3 ring mains and cooker circuits on the other side. originally i got called out for a tripping mcb and rcd on the kitchen ring when they overloaded the ring. did a quick check on the Zs and got 4.56 from every socket in the kitchen - then did a check on the other rings on the RCD, all about the same figure. did a Ze test (all good 0.18). stripped down the neutral busbar and earths from the mcbs and did a Zs test on the busbar (4.56 again) changed RCD but still same problem. meggered the rcd circuits - all good apart from kitchen ring L-PE 85.4Ohms on 500v - but still shouldnt cause such high results on the other Zs? any suggestions?? apparantly no pictures hooks or nails have been banged in either.