Being cross-bonded guarantees its all at the same voltage, not necessarily 0V though. If you have a meter, measure between the sink and a 'real earth' (hammer a bit of pipe into the garden for this test - alternatively the metal blade of a spade stuck in with a bucket of water thrown over it will do.)
This temporary earth will be high impedance (perhaps 1000 ohms plus) so expect to be able to measure volts on a digital meter, but maybe not to be able to light test lamps etc.
If there is more than 10V measured, then repeat the test to the main earth (MET) at the fuseboard - if this is not the same voltage then your kitchen wiring earths don't actually make it back to the MET, look for the break.
But if the MET is also a bit live, we need to know if you have PME/TNC or TT main earthing (see for reference at top of forum). If TT, your earth spike has rusted through and should be replaced, while if it is PME or TNS, contact your local DNO (see for reference again.)
hope that gets you started
M.