Putting in the first fix electrics, then getting a local spark to do the second, test and part P cert.
I have:
~10m internal 6mm T&E from the fuse box to an external junction
~10m of 6mm SWA, partly clipped to a wall in PVC conduit and partly buried.
Into the shed. Junction box and 3 double sockets on 2.5mm 3core and fused spur to 50W Fluor light using 2.5mm too.
The shed is likely to have small freezer or fridge freezer, heater now and then, TV, Stereo and the odd power tool. Questions are:
1. Does all that sound about right or do I need 10mm T&E and SWA. And maybe lesser in the shed T&E rather than 3 core?
2. Do any of the junction boxes need fuses?
Cheers