I am told the DNO can set up multi-feeds with fuses drawn or inserted so they can isolate sections to work on them. Not in all cases, but we who don't work for the DNO will not know if the supply has changed.
So we are also told TN-C-S domestic is at least 0.35Ω and TN-S is at least 0.8Ω non domestic is a different kettle of fish. So where the incomer is say 0.25Ω should we allow for the supply to change due to DNO using different routes so a 32A supply instead of being 1.37Ω would need to be 1.27Ω to allow for the change in the incomer.
I think the 0.35Ω is (230 volt * 10% + 230 volt * 6%)/100 = 0.368Ω so it is the worst ELI line to neutral/earth that will be within the volt drop allowed.
So we are also told TN-C-S domestic is at least 0.35Ω and TN-S is at least 0.8Ω non domestic is a different kettle of fish. So where the incomer is say 0.25Ω should we allow for the supply to change due to DNO using different routes so a 32A supply instead of being 1.37Ω would need to be 1.27Ω to allow for the change in the incomer.
I think the 0.35Ω is (230 volt * 10% + 230 volt * 6%)/100 = 0.368Ω so it is the worst ELI line to neutral/earth that will be within the volt drop allowed.