Just started PIR on an installation at a local farm/stables/tack room/feed barn today. Looks like it could be a fairly long/fiddly job...
Today was a metal workshop with a fairly simple set up. However, I'm not 100% sure on the position with equipotential bonding to the structure.
The entire structure is metal, and therefore clearly an extraneous conductive part. Therefore I would consider it should be bonded and will note such on the PIR, most likely as a code 2. However, I'm not sure how such bonding would be installed in practise.
Since they have an 'electrician' on the staff who will do any of the remedial work they will likely ask what needs doing so any practical advice welcomed.
The structure is simple metal RSJs bolted together and clad, but would it be normal to separately bond every beam, or trust the bolted connections to ensure continuity? The work involved in bonding every individual piece would be substantial, and the testing of their effectiveness likewise.
For a TT system, it had a remarkably good earth (1.92Ohm) considering where the earth rod is:
In general the installation is pretty good considering - RCDs are in place, and the wiring in the workshop at least is all SWA. The only 'slight' issues I found were 2.5mm cable run from a 32A MCB and swapped neutrals on the two light circuits
Mind you, this is what I still have to look at next so who knows what joys I shall discover.
Gavin
Today was a metal workshop with a fairly simple set up. However, I'm not 100% sure on the position with equipotential bonding to the structure.
The entire structure is metal, and therefore clearly an extraneous conductive part. Therefore I would consider it should be bonded and will note such on the PIR, most likely as a code 2. However, I'm not sure how such bonding would be installed in practise.
Since they have an 'electrician' on the staff who will do any of the remedial work they will likely ask what needs doing so any practical advice welcomed.
The structure is simple metal RSJs bolted together and clad, but would it be normal to separately bond every beam, or trust the bolted connections to ensure continuity? The work involved in bonding every individual piece would be substantial, and the testing of their effectiveness likewise.
For a TT system, it had a remarkably good earth (1.92Ohm) considering where the earth rod is:
In general the installation is pretty good considering - RCDs are in place, and the wiring in the workshop at least is all SWA. The only 'slight' issues I found were 2.5mm cable run from a 32A MCB and swapped neutrals on the two light circuits
Mind you, this is what I still have to look at next so who knows what joys I shall discover.
Gavin