Good morning all,
My mother had a new Potterton Suprima 30L Boiler fitted about 3 months ago and has had constant problems with it. Thankfully most have been sorted but one fault remains which the installers seem incapable of curing.
The problem is as follows:
When the system comes on in the morning all is fine (but see note!!), the boiler switches on normally, the water in the cylinder heats up and the radiators warm up. However, when the water cylinder thermostat switches off, the boiler goes berserk - the red/green leds on the control panel flash on and off like christmas tree lights not following any sequence at all and the boiler switches on and off every few seconds.
To cut a long story short, a bloke from potterton came to sort it out at the request of the installer, and he says that the problem is the 'switching live'
voltage at the boiler dropping to approx 190-210v in the 'fault' condition
which is apparently insufficient to fire the boiler hence the erratic LED
sequence and boiler operation. He spoke to the installer and suggested a wiring fault and I am now waiting for the contractors Electrician to attend.
As the Electrician has been back on two occasions already without success
I do not have a great deal of confidence in him to sort it out on his next visit, although I am assured he is well qualified...
My own checks/observations are:
1/ The 240v switching voltage measured at the room thermostat appears
OK and switches on/off normally as measured with a meter.
2/ The switching voltage at the boiler ONLY drops off when the cylinder
thermostat switches off.
3/ The operation of the 3-way motorised valve actuator appears fine
(I have lifted the actuator off the valve and observed its operation and checked the free movement of the valve spindle) but NOTE that the radiators still get hot even if the room thermostat is set at Zero!
I assume this is caused by leakage through the valve and does not particularly concern me unless of course it is contributing to the fault.
I would very much appreciate any input/comments/suggestions as this is driving me barmy!
Thanks for reading....
Sailor
++++
My mother had a new Potterton Suprima 30L Boiler fitted about 3 months ago and has had constant problems with it. Thankfully most have been sorted but one fault remains which the installers seem incapable of curing.
The problem is as follows:
When the system comes on in the morning all is fine (but see note!!), the boiler switches on normally, the water in the cylinder heats up and the radiators warm up. However, when the water cylinder thermostat switches off, the boiler goes berserk - the red/green leds on the control panel flash on and off like christmas tree lights not following any sequence at all and the boiler switches on and off every few seconds.
To cut a long story short, a bloke from potterton came to sort it out at the request of the installer, and he says that the problem is the 'switching live'
voltage at the boiler dropping to approx 190-210v in the 'fault' condition
which is apparently insufficient to fire the boiler hence the erratic LED
sequence and boiler operation. He spoke to the installer and suggested a wiring fault and I am now waiting for the contractors Electrician to attend.
As the Electrician has been back on two occasions already without success
I do not have a great deal of confidence in him to sort it out on his next visit, although I am assured he is well qualified...
My own checks/observations are:
1/ The 240v switching voltage measured at the room thermostat appears
OK and switches on/off normally as measured with a meter.
2/ The switching voltage at the boiler ONLY drops off when the cylinder
thermostat switches off.
3/ The operation of the 3-way motorised valve actuator appears fine
(I have lifted the actuator off the valve and observed its operation and checked the free movement of the valve spindle) but NOTE that the radiators still get hot even if the room thermostat is set at Zero!
I assume this is caused by leakage through the valve and does not particularly concern me unless of course it is contributing to the fault.
I would very much appreciate any input/comments/suggestions as this is driving me barmy!
Thanks for reading....
Sailor
++++