No, external chargers have had that problem.its the charger built into the car that is sensitive to a volt drop
If I understand what is being said correctly, there seems to be a bit of a difference of opinion here (regardless of whether the charger is internal or external to the car) - you are describing 'a problem', but ChewChew seems to be calling it a 'safety feature'.No, external chargers have had that problem.
Maybe.I suspect ChewChew believes what the adverts tell him.
Rather more than warm - T&E is rated for use at 70C.It's ok, and I appreciate that cables can warm up in use,
Just to clarify, that's the conductor temperature.T&E is rated for use at 70C.
As flameport has said 6mm² T&E is 'rated' at 70°C. I've never been certain, but I presume the implication is that the tabulated CCCs we use indicate (undoubtedly with some 'safety margin') the current which, with the installation method in question, "will" raise the conductor temp from 30°C to 70°C. On that basis 6mm² 'clipped direct' should get to something approaching 70°C (a 40°C rise from the assumed ambient of 30°C) at a current of 47A. That being the case, your 40-45°C (a temp rise of 10-15°C from that assumed ambient) doesn't sound far off what I would expect..... it's not often in a domestic setting that you see such a big load carried for so long... Induction hob, electric showers etc.. are far more short bursts of power, so you don't see the heating effect. The cable probably gets to maybe 40-45C max, but as I said, if I was to fit one again, and if I was using T&E, then I'd use 10mm to reduce the heating effect.
Not always.Admittedly, your ambient is presumably going to be far less than the assumed 30°C