Any thoughts on this question:
As this has not been covered in the course notes, I assume we would be expected to look up the curves in the Regs book?
I was wondering if what they are getting at is that 9.3X rated current on a type D and C would be in the region where the thermal trip will operate but for a B type, the magnetic trip would operate, so type B would be fastest?
Which one of the following devices will disconnect in the fastest time if a short circuit current of approximately 300A occurred on a circuit? | |
a) | 32A/30mA Type C RCBO |
b) | 32A Type B circuit breaker |
c) | 32A Type C circuit breaker |
d) | 32A Type D circuit breaker |
As this has not been covered in the course notes, I assume we would be expected to look up the curves in the Regs book?
I was wondering if what they are getting at is that 9.3X rated current on a type D and C would be in the region where the thermal trip will operate but for a B type, the magnetic trip would operate, so type B would be fastest?