The rule book says your allowed 3% volt drop for lighting, and 5% for everything else, I would not expect an inspector to worry about volt drop, however in the main a conservatory means the LABC can stick their noses in, so dotting i's and crossing t's may be required.
There are many ways to extend a ring final, but in theory first step is to measure the loop impedance to see if near the limit or not, that is all well and good for an electrician with a loop impedance meter, but without that meter the safe option so not to exceed the impedance limits is the fused connection unit (FCU).
Since it is from a ring final, you can't really have a new circuit even if by definition a circuit is "An assembly of electrical equipment supplied from the same origin and protected against over current by the same protective device(s)." as that would not make sense in English to have a final final. So you can with the exception of special locations fit a fused spur from a ring final without notifying, and the limits for a 13 amp fuse is 2.42 Ω so unlikely to exceed the limit when the ring final is 1.44 Ω, so the FCU is likely the best option.
Using a grid system you can have a single socket and a fuse in a double socket back box, which is how I extended a spur.

I use
Screwfix LAP range. There is enough room for two fuses and a socket so could take both lights and sockets from that, and still have a socket. The advantage is your unlikely to exceed the loop impedance limits.
If actually extending the ring, the limit for lights is 16 amp, so you could use a switched FCU as the light switch and a 3 amp fuse.