If 1 light works and the other two are part of the same circuit it would tend to indicate that the light fittings may have died.
Have you a multi meter and are you comfortable with testing live electrical service?
If not, call someone in who is!
If you are okay with it then:-
Main fuse at CU- Does the 2 faulty lights run on the same circuit as the one that works?
(if so, the fuse must be 'good' otherwise the working lamp wouldn't)
Open the covers of the light fittings and test for voltage across the live / neutral.
If both fittings have power, then the fittings have failed. If neither fitting has power then you have a wiring fault.
It becomes difficult to add to this further since you haven't explained the wiring set up.
Does each light have a seperate light switch or are there 3 switches, one for each light?
Do the lights make up part of the main lighting circuit? or
Do the lights come via the ring main and have a fused spur box between the ring live and the lights (if so has the fuse gone?)?
Please expand on your detail regarding the set up, and I'm sure someone will try to help, maybe even me