I have rewired my house fully with the exception of the consumer unit which was replaced 3 years ago.
Friday was my second LABC visit for a final inspection and sign-off.
He checked the main earth, earthing via gas and water pipes, earth on ring final circuits and RCD disconnect values and times.
The inspector complemented my work as said it was to a high standard, however I failed the inspection because:
1) The RCD in the consumer unit (Square D Dom63R30) tripped at 33ms according to his tester
2) I had not sealed the holes in the top of the CU.
I will replace the RCD when I can find a spare, any idea where to get one from?
When I had the CU replaced he left the holes in the top of the CU unsealed, I cannot get my little finger in them due to the cables. The LABC inspector wants me to seal them with 'something', what something should I use? He suggested silicone sealant.... this seems over the top to me.
Any advice please?
Friday was my second LABC visit for a final inspection and sign-off.
He checked the main earth, earthing via gas and water pipes, earth on ring final circuits and RCD disconnect values and times.
The inspector complemented my work as said it was to a high standard, however I failed the inspection because:
1) The RCD in the consumer unit (Square D Dom63R30) tripped at 33ms according to his tester
2) I had not sealed the holes in the top of the CU.
I will replace the RCD when I can find a spare, any idea where to get one from?
When I had the CU replaced he left the holes in the top of the CU unsealed, I cannot get my little finger in them due to the cables. The LABC inspector wants me to seal them with 'something', what something should I use? He suggested silicone sealant.... this seems over the top to me.
Any advice please?