Greetings all,
I have just moved into a new house. The electrical installation seems fairly new. the CU is a Wylex split load. The main switch is a 100 amp/100 ma time delay RCD. The sockets and immersion heater are protected by a 80A/30ma RCD. The earthing system appears to be TN-S ( the earth comes from the sheath of the incoming power cable).
The 30ma RCD trips when the test button is pressed. The main switch does not trip when the test button is pressed, but does turn the power off when it is switched off.
From my research in this forum and other sites it seems that it is not necessary to have an RCD on the main switch for a TN-S installation. A replacement for this time delay RCD is very expensive. Is it really necessary? Could I leave it as it is or replace it with something cheaper?
I would be really grateful for some advice
Steve
I have just moved into a new house. The electrical installation seems fairly new. the CU is a Wylex split load. The main switch is a 100 amp/100 ma time delay RCD. The sockets and immersion heater are protected by a 80A/30ma RCD. The earthing system appears to be TN-S ( the earth comes from the sheath of the incoming power cable).