set the scene:
new shop.
sales floor with 70-80 no. 4 x 14w T5 fittings.
warehouse with 12 no. 4 x 18w T8 fittings with prismatic diffusers.
canteen with 4 (same as warehouse) fittings
office with 2 (same as w/hse) fittings, but with reflectors.
All fittings have electronic instant start ballasts. All back area fittings controlled by PIRs.
office - tubes went black at ends quickly, both fittings flickered for a while, one after the other, then stopped working intermittently. New tubes fitted, still flickering. Ballasts on order.
canteen - one fitting after another went, this was before the office, but in the same fashion. Again, tubes badly blackened. All 4 relamped, two ballasts failed, replaced by digital ballasts. One of these is now struggling to maintain illumination.
warehouse - only one so far needed tubes, but a couple of fittings showing blackened ends.
shop floor - extensive relamping carried out, several ballasts replaced (though only half the shop floor).
What could be wrong? The only common factor is the mains supply, and the DB. I can see this carrying on indefinitely. Something is killing ballasts and tubes left right and centre. Store been open 4 months.
Sparks came yesterday to do a report, and tightened all the terminations in the DB, every single one could be tightened, they wrenched all the connections very tight. Voltages tested, ok. Internal wiring all ok.
The PIRs are the contact variety - not solid state. You can hear them click on/off, so this should have no effect on the fittings.
Anyone come across anything like this before? I know we have a few good problem solvers on here.
new shop.
sales floor with 70-80 no. 4 x 14w T5 fittings.
warehouse with 12 no. 4 x 18w T8 fittings with prismatic diffusers.
canteen with 4 (same as warehouse) fittings
office with 2 (same as w/hse) fittings, but with reflectors.
All fittings have electronic instant start ballasts. All back area fittings controlled by PIRs.
office - tubes went black at ends quickly, both fittings flickered for a while, one after the other, then stopped working intermittently. New tubes fitted, still flickering. Ballasts on order.
canteen - one fitting after another went, this was before the office, but in the same fashion. Again, tubes badly blackened. All 4 relamped, two ballasts failed, replaced by digital ballasts. One of these is now struggling to maintain illumination.
warehouse - only one so far needed tubes, but a couple of fittings showing blackened ends.
shop floor - extensive relamping carried out, several ballasts replaced (though only half the shop floor).
What could be wrong? The only common factor is the mains supply, and the DB. I can see this carrying on indefinitely. Something is killing ballasts and tubes left right and centre. Store been open 4 months.
Sparks came yesterday to do a report, and tightened all the terminations in the DB, every single one could be tightened, they wrenched all the connections very tight. Voltages tested, ok. Internal wiring all ok.
The PIRs are the contact variety - not solid state. You can hear them click on/off, so this should have no effect on the fittings.
Anyone come across anything like this before? I know we have a few good problem solvers on here.