Would like a second opinion please
Three days ago, I did a small amount of socket moving. Basically:
* Blank faceplate, where the original socket position was blocked by the old boiler.
* Cables running through chocblocks in this faceplate, and down to a surface mounted backbox.
I removed the blank faceplate and original backbox & substituted for a 2x singles backbox.
I then terminated cable #1 into a FCU on the first position. Cable was very tight, so I elected to terminate cable #2 into chockblocs, and then install links to a single socket and the FCU.
A little messy, but nothing AFAIK wrong with it.
All of these links I did with a small section of the inner cores of the original T+E salvaged from running down to the surface mounted backbox, with the reasoning that it was better to keep the color scheme consistant within the socket.
I checked for stray voltages and misplaced continuity between cables, and then put everything back together, followed by a voltage test at the socket & FCU- everything looked normal.
Last night then, the breaker for these sockets (16a radial) & by extension the main RCD tripped.
Opening up the socket again, I found a discolored section on the linked live, which when removing the wire pretty much snapped.
I've replaced the three wires from the offending link with a brand new section of T+E, and all appears well again.
I'm thinking faulty wire, either a nick in the insulation, or snapping when bent by the frontplate. *Don't* think I nicked it with the screws or between the backbox and frontplate, but it's always a possibility.
Apologies for the essay, but would appreciate a second opinion on what went wrong. Replacing the whole lot including stuff in the walls is obviously a possibility, but one I'd obviously like to avoid, as that goes well outside my area of comptence as a reasonable DIY-er
Three days ago, I did a small amount of socket moving. Basically:
* Blank faceplate, where the original socket position was blocked by the old boiler.
* Cables running through chocblocks in this faceplate, and down to a surface mounted backbox.
I removed the blank faceplate and original backbox & substituted for a 2x singles backbox.
I then terminated cable #1 into a FCU on the first position. Cable was very tight, so I elected to terminate cable #2 into chockblocs, and then install links to a single socket and the FCU.
A little messy, but nothing AFAIK wrong with it.
All of these links I did with a small section of the inner cores of the original T+E salvaged from running down to the surface mounted backbox, with the reasoning that it was better to keep the color scheme consistant within the socket.
I checked for stray voltages and misplaced continuity between cables, and then put everything back together, followed by a voltage test at the socket & FCU- everything looked normal.
Last night then, the breaker for these sockets (16a radial) & by extension the main RCD tripped.
Opening up the socket again, I found a discolored section on the linked live, which when removing the wire pretty much snapped.
I've replaced the three wires from the offending link with a brand new section of T+E, and all appears well again.
I'm thinking faulty wire, either a nick in the insulation, or snapping when bent by the frontplate. *Don't* think I nicked it with the screws or between the backbox and frontplate, but it's always a possibility.
Apologies for the essay, but would appreciate a second opinion on what went wrong. Replacing the whole lot including stuff in the walls is obviously a possibility, but one I'd obviously like to avoid, as that goes well outside my area of comptence as a reasonable DIY-er