FCU for wall display light: replace with double socket

Joined
16 Mar 2005
Messages
491
Reaction score
14
Country
United Kingdom
In my living room, a spur from the ring main runs to a FCU near the skirting board. From the FCU, cable runs up a chase in the wall to a wall unit/feature display lamp, which is operated via a switch adjacent to the FCU.

I don't use the wall lamp and plan to replace the FCU with a single or double socket, giving me access to extra sockets on that particular wall.

Any problems with doing this?

Thanks
Bruce
 
Sponsored Links
No, should be fine, but make sure the previous installer used full size (2.5mm) cable to come from the ring, and add no more than one 13A load to one spur. Note that a double socket counts the same as a single 13A one for this purpose.

If adding more sockets, you will need to break into the ring properly

Like this pair of before and after pictures.

RingMainExtension.jpg


Here's hoping he doesn't mind his picture being lifted.
regards M.
PS cables to be routed in approved methods - see 'for reference' at top of forum.
 