FCU to step down amp rating

Joined
27 Jun 2023
Messages
16
Reaction score
2
Country
United Kingdom
Hi all,

Question around using multiple FCUs in a circuit.

I've drawn some pictures to illustrate what I currently have and what I'd like to do, all dependent on whether it's safe/allowed!

Currently I have a direct line from the CU to a small 3a fcu that feeds the alarm backup module.

I want to put a small fridge in this cupboard and this line out is the easiest to access.

Can I add a further FCU, at 13a with a double socket spurred off by tapping in to this line. Then continue the wiring from the 13a FCU (load side) to the 3a FCU that then feeds the alarm module.

The pictures may help explain better.

Thanks in advance.
20231216_201656.jpg


20231216_201704.jpg
 
Sponsored Links
Thanks for the response, not sure if this answers your question, but this is the circuit it would be pulled from:

20231216_203651.jpg
 
Sponsored Links
What do you mean by :
Currently I have a direct line from the CU
That MCB is marked as ground floor sockets and
It would be easy to assume you have a whole ring or radial circuit on that MCB of which just one point is your
small 3a fcu that feeds the alarm backup module.
something like this:
1702771355003.png

IF that is the case then adding a double socket would not require a FCU, either by adding:
Spur from existing FCU live side:
1702771991867.png


Or adding it into the ring (Or radial as appropriate):
1702772466176.png


However first you will need to ascertain exactly what you currently have.
 
Thanks for the reply.

I've opened it up to check.

Ring goes off from bottom of box to sockets. T&e Wire out, wire in.
Alarm circuit comes off as a single radial circuit wired in to the same mcb as a standalone.

Again, I've tried to draw to illustrate... bear with me
20231217_104928.jpg
 
Your original proposal , introducing a FCU with 13 amp fuse is ok ,but you should connect the new socket and the alarm FCU to its load terminals.
 
Thankfully it looks to be run in 2.5mm T.E, I've got a spool in the shed so can keep it all the same gauge!
 
Thankfully it looks to be run in 2.5mm T.E, I've got a spool in the shed so can keep it all the same gauge!
One option and probably the easiest, although frowned upon for reliability of the alarm system would be to replace the FCU with a double socket and plug the alarm into it:
1702840659135.png

As Terry has already mentioned, this is arrangement is correct:
1702841348677.png
 
Of course another option would be to fit an additional MCB (16A) in the CU rather than a 13A FCU, however that would be creating a circuit and require the raising of paperwork.
 