Went to a sigma 60-100 gc 41-267-19
no life, and not sending live feed to pump. Measured thermister to eliminate it from my enquiries as many pcb's won't go on to anything if thermister is out of range at the start, and it was over 1.5meg. Emailed Ferroli who responded
"thermister should be 1 meg, if not 230v from grey lead on X5 it's thermister or pcb."
So I took a 1 meg resistor to job, replaced thermister with it, and boiler worked, let it get warm.
Then the funny thing, put thermister back in circuit and it's now working.
My thoughts are that the change in temperature I forced by starting the boiler on a resistor has kicked the thermister into life. I presume though that it is a knackered thermister and shall get one on order right away.