The boiler: ferroli falcon probably mark I.
The problem: lock out light comes on requiring reset; sometimes in heating mode sometimes in dhw mode.
When: usually after several hours working, but once gone in to lock out mode a second reset needed after only ten minutes. Once the boiler has to be reset it is usually a matter of resetting it for the rest of the day.
Tests done so far:
Valve. Modulates fine between 2 and 12 mb. Heating is range rated to minimum.
Inlet pressure fine.
Continuity between sensing electrode and board connection: less than 1 ohm.
100 degree stat is replaced, and has heat conducting paste on it.
System pressure is constant and never needs topping up.
Polarity is fine.
Boiler is about 5 years old.
No noticable blockage of the rads, they heat up quickly and completely from top to bottom.