Hi
After searching on here and elsewhere I have come to a dead end fault finding my boiler.
It is an FER Falcon approx 3 1/2 years old.
Yesterday there was a powercut and after that the CH stopped working on this boiler. The DHW works perfectly so I know there is nothing fundamentally wrong with the boiler or pcb.
I have replaced the external thermostat link to eliminate that problem.
I have swapped the CH and DHW thermistors which made no difference. Oddly, unplugging the CH thermistor starts the CH working (CH pump, fan and burner) for about 10-15 seconds after which it goes back to CH standby (blinking CH lamp). It then does nothing unless you unplug the CH thermistor again. Both relays are clicking healthily and the pump and fan both run.
What do I check next?
Many thanks
Ian
After searching on here and elsewhere I have come to a dead end fault finding my boiler.
It is an FER Falcon approx 3 1/2 years old.
Yesterday there was a powercut and after that the CH stopped working on this boiler. The DHW works perfectly so I know there is nothing fundamentally wrong with the boiler or pcb.
I have replaced the external thermostat link to eliminate that problem.
I have swapped the CH and DHW thermistors which made no difference. Oddly, unplugging the CH thermistor starts the CH working (CH pump, fan and burner) for about 10-15 seconds after which it goes back to CH standby (blinking CH lamp). It then does nothing unless you unplug the CH thermistor again. Both relays are clicking healthily and the pump and fan both run.