Right. Got a complete fud of a problem and looking for some ideas.
I have a Ferroli Modena 102 combi which has concentric flue.
When we bought the house, the boiler was cutting out when running hot water. Had a firm out who said the fan needed replaced. After the fan was replaced, which was maybe 18 months ago, the issue seemed to be sorted.
However it has always sounded a bit "chuffy" in that it sounds like it is trying to pull air in. It was due a service and a friend is a boiler engineer so asked if he could take a look. The seal on the combustion chamber had broken away at one point which would have allowed air to be sucked in plus a gasket on part of the flue was misformed. He replaced both of those with new Ferroli parts and after putting the case back on it started making a very strong shaking sound. Cracking the case open stopped it and it was clear air was being pulled in through the open case.
The fan has been removed and it runs perfectly smoothly.
So he has checked the flue, which is within the 4m max vertical length, the part that comes out the roof also seems fine. The flue I think is 4" diameter (or if not it is what the Ferroli manual states is right).
It is clearly an airflow problem but he cannot see why, short of replacing the flue with a 5" one.
Makes me wonder if this has always been a problem with the boiler and the previous owner found that removing a bit of the seal worked, or just loosened the case a bit to let enough air in.
Short of replacing the flue, any ideas that we could try? Don't want to waste any more of my mates time!
Cheers.
I have a Ferroli Modena 102 combi which has concentric flue.
When we bought the house, the boiler was cutting out when running hot water. Had a firm out who said the fan needed replaced. After the fan was replaced, which was maybe 18 months ago, the issue seemed to be sorted.
However it has always sounded a bit "chuffy" in that it sounds like it is trying to pull air in. It was due a service and a friend is a boiler engineer so asked if he could take a look. The seal on the combustion chamber had broken away at one point which would have allowed air to be sucked in plus a gasket on part of the flue was misformed. He replaced both of those with new Ferroli parts and after putting the case back on it started making a very strong shaking sound. Cracking the case open stopped it and it was clear air was being pulled in through the open case.
The fan has been removed and it runs perfectly smoothly.
So he has checked the flue, which is within the 4m max vertical length, the part that comes out the roof also seems fine. The flue I think is 4" diameter (or if not it is what the Ferroli manual states is right).
It is clearly an airflow problem but he cannot see why, short of replacing the flue with a 5" one.
Makes me wonder if this has always been a problem with the boiler and the previous owner found that removing a bit of the seal worked, or just loosened the case a bit to let enough air in.
Short of replacing the flue, any ideas that we could try? Don't want to waste any more of my mates time!
Cheers.