Hi folks,

In a recent thread, I've been trying to find the answer to a question I've been asked about the difference between two FireAngel smoke alarms. However, not only have I not yet got an answer to that question, but my thread rapidly got sidetracked into a discussion about the merits (or otherwise) of FireAngel products in general.

Since no-one has yet been able to answer my question, it's probable that no-one my ever be able to(so I may try asking FireAngel). However, this exercise has caused me to look and think a fair bit about the issue of fire alarm batteries in general, which leaves me fairly confused. - so I wonder if anyone might be able to help to educate or un-confuse me! My comments/questions are as follows ...

1... There are plenty of battery-only fire alarms around which use a 9V non-rechargeable alkaline battery (typically about 550 mAh), which is expect to last for a year or more. That implies an average consumption of around 0.06 mA. The actually current draw may well be intermittent, such that it is much greater than that when current is being drawn, but it would nevertheless be surprising if the 'peak' current (whilst it was being drawn) were more than, at most, a small number of mA.

2... Mains-powered alarms are usually powered by the mains but have battery back-up. When the battery is rechargeable (usually lithium-ion), the situation is pretty straightforward - the alarm is usually powered by the mains, and the battery is kept charged so that it will always be more-or-less fully charged, and hence able to 'take over' should there ever be a mains power failure.

3... My confusion arises when the battery in not rechargeable - either alkaline (typically 550 mAh) or lithium metal (typically 1,200 mAh). Both usually have shelf lives of about 10 years, and are said by the alarm manufacturers to be able to last for at least 1 year and 10 years respectively.

4.... When a non-rechargeable battery is used as the backup, it is not literally 'doing absolutely nothing' in the absence of a mains failure. Whiilst it would be possible to monitor the 'no load' voltage of a battery with virtually no current drain from it, there is presumably a need to monitor its voltage when supplying the 'peak' current that may be needed to run the alarm - so, I would imagine, at most, 'a few mA for a few seconds', occasionally.
If an alkaline battery can, alone, actually run an alarm continuously for a year or more, I find it very hard to understand why it should not last a lot more than a year (potentially its entire shelf-life) when supplying only "at most, 'a few mA for a few seconds', occasionally". On the basis of what I've said, I would have expected an alkaline back-up battery to last for it's entire shelf-life (which could be 10 years), hence quite possibly rendering it unnecessary to consider a non-rechargeable lithium one. What am I missing?

Can anyone help me understand?

Kind Regards, John
 
4. I have some in this category. AICO. The batterys last very approx 5 years or more. I wonder to myself, what is the point of having a mains connection?
The dam things beep when battery low. The only good thing about having mains ones, it that they are interlinked.

I think the answer is the regulations say they need a mains connection
 
4. I have some in this category. AICO. The batterys last very approx 5 years or more. I wonder to myself, what is the point of having a mains connection?
The dam things beep when battery low. The only good thing about having mains ones, it that they are interlinked.

I think the answer is the regulations say they need a mains connection

Which regulations are they ?
 
Which regulations are they ?
We've been through this before. I don't think that (even in Scotland) there are any regulations requiring alarms to be mains-powered, but there is 'guidance' to that effect. In fact, Scotland (where the regulations are tighter) explicitly allows 'sealed battery' ones (although they do insist on interlinking and specify a minimum number of locations) ....

Scottish Government said:
There are 2 types of interlinked fire alarms that meet the new rules:
  • sealed battery alarms – which should be tamper-proof long-life (which can be up to 10 years) batteries. You can fit these alarms yourself.
  • mains-wired alarms - these are cheaper than tamper proof long-life battery alarms, but should be installed by a qualified electrician. These should be replaced every 10 years.
Both types of alarm are interlinked by radio frequency without the need for WiFi.
 
4. I have some in this category. AICO. The batterys last very approx 5 years or more.
Yes, as I said, I would expect at least that long, but the manufacturers always seem to say 1 year for alkaline batteries.
I wonder to myself, what is the point of having a mains connection?
The dam things beep when battery low. The only good thing about having mains ones, it that they are interlinked.
They don't have to be mains powered to be interlinked - most 'sealed battery' ones can be interlinked wirelessly (and some by hard wring)
I think the answer is the regulations say they need a mains connection
As I've just written, that seems to be a myth, even in Scotland (where regs are tighter).
 
I think the confusion with the regs are between a rented property and a non rented property -- perhaps
 
You may think wireless ones would be heavier on batteries. Unless they only talk on an alarm condition. That would be too much to hope for.
 
We've been through this before. I don't think that (even in Scotland) there are any regulations requiring alarms to be mains-powered, but there is 'guidance' to that effect. In fact, Scotland (where the regulations are tighter) explicitly allows 'sealed battery' ones (although they do insist on interlinking and specify a minimum number of locations) ....

In Woking they like to see a minimum of 1 unit being mains powered. The others can be battery RF linked to the main unit

Why the people writing these regs can’t just make the requirement crystal clear is beyond me

Then people wonder why unfortunate incidents like Grenfelll happen
 
I think the confusion with the regs are between a rented property and a non rented property -- perhaps
That may well be true - I did not specifically look for anything about rental properties The Scottish law I quoted (which explicitly allowed non-mains alarms, provided they were interlinked) related to all domestic dwellings, so there might be even tighter regs for rental properties.

I'll see what I can find.
 
You may think wireless ones would be heavier on batteries. Unless they only talk on an alarm condition. That would be too much to hope for.
I don't really see why they would need to talk other than there was an alarm condition. The hard-wired interlinks certainly merely put a voltage on the 'interlink' line when there is an alarm.
 
In Woking they like to see a minimum of 1 unit being mains powered. The others can be battery RF linked to the main unit ...
Hmmm !
Why the people writing these regs can’t just make the requirement crystal clear is beyond me. Then people wonder why unfortunate incidents like Grenfelll happen
I agree with your general comment but, if I have understood correctly, in the case of Grenfell I think the regs were clear enough, but 'wrong'.
 
I think the confusion with the regs are between a rented property and a non rented property -- perhaps
Looking at ....

1737741910795.png


.... I find ....

The regulations do not stipulate the type of alarms (such as mains powered (‘hard-wired’) or battery powered) that should be installed.

We recommend that landlords choose the type of smoke alarms based on the needs of their building and their tenants, and that those alarms are compliant with British Standards BS 5839-6. Where battery powered alarms are selected, alarms with ‘sealed for life’ batteries rather than alarms with replaceable batteries are the better option.

.... and ....

The regulations do not stipulate where the alarms should be placed.

At least one smoke alarm should be installed on every storey which is used as living accommodation.

Landlords should follow the individual manufacturer’s instructions when installing the alarms. However, in general, smoke alarms should be fixed to the ceiling in a circulation space, i.e. a hall or a landing.

.... so (unless things have changed since 2022) no requirement for mains-powered - in England. That leaves Wales and Scotland (and NI) to be considered!
 
Hmmm !

I agree with your general comment but, if I have understood correctly, in the case of Grenfell I think the regs were clear enough, but 'wrong'.

The regs were not clear enough. That’s what the enquiry concluded IIRC
 