Thanks John, it will be joined into 32A existing ring circuit which goes back to the MK Sentry consumer unit with individual trip fuses. It is a straight replacement of the exist kitchen power, plus adding three new sockets into the new dining area.
Any new buried cables and any new sockets are required to have RCD protection. Is the circuit in question protected by an RCD(a wide device with a test button) in your consumer unit? If all the work consists of an extension of an existing circuit, it shoud not be 'notifiable' work.
I have read about the safe zones but in the kitchen the power will come down all along the wall so I can protect with channelling there?
If cables were buried (<50mm deep) and
not in 'safe zones' then protecting them with 'channelling would not be adequate - you would either have to use special cable or else run the cables in earthed steel conduit. Perhaps you could explain more about "power coming down all along the wall"? Each socket creates safe zones horizontally and vertically aligned with them - so if a cable ran vertically down a wall into a socket, it would probably be in a safe zone.
Kind Regards, John