I have had a T&G floor delivered 6mtr x 3.6mtr that was spec'd to be 19mm T&G. What arrived was 16mm T&G.
The floor is supported on 38x75 joists running lengthways 6mtrs. The joists are set at outside edge then 600mm-joist-390mm-joist-600mm-joist-390mm and so on alternate across the width of 3.6mtr.
The floor seems to be uncomfortably springy over the 600mm spans.
Can someone with tables let me know what the difference in floor acceptable loading would be as is with 16mm T&G and also with the spec'd 19mm T&G.
Thanks in advance.